Export schedule - Failed to set inverter schedule for export to grid.
Doesn't that mean that unless your battery is charged to 99% and there's 10kWh of ssolar gain forecast for the next day then it won't meet the criteria so won's set a schedule?
Found the cause of the export schedule failing to set: I have an Export Limit set on my SPH inverter of 60%. When I disabled this setting I could then manually set the grid first setting. I'll leave it off and will check that the WW export schedule works tomorrow.
I have asked Growatt support if its expected that grid first can't be set when there is an export limit configured.
To complete the thread, Growatt support confirmed that "grid first" (aka export) cannot be configured if there is an export limit set. Typically an export limit is used to restrict the amount of power exported to the grid if the PV/battery/inverter system is capable of exporting more than is allowed by the grid installation.