I set an Export to Grid schedule yesterday with a window of 21:30 to 23:30 and a stop at 10% SOC. When I checked later in the evening the export had started at the correct time but stopped when the SOC reached 25% and recommenced importing from the Grid.
I notice the log says " Export to grid instruction set for 21:30 - 23:18 (adjusted)."
I have looked through various settings on WW and can't see anywhere I've set a " Smart " charge / discharge condition. I've checked under settings in the Inverter section on the GivEnergy portal and can't see anything I've set there either. Can you check if I've done something in the background please.
Spirited-Drag
Timed Export to Grid slot truncated
- Edited
but stopped when the SOC reached 25% and recommenced importing from the Grid.
It doesn't check the percentage, the adjusted time is simply based on the calculation of the max discharge rate over time. This will then be used instead of your original end time to stop. This is basically our alternative way to prevent users drawing from the grid after their battery has reached target SOC, without us having to continuously poll for your SOC.
What should happen is, that Eco should be enabled at this point, or shortly afterwards.
We will look into that.
OK - so looking at our diagnostics logs, we did send a successful Eco reset at 23:16 - see:
You should also see this in your Giv log.