Release 441 - Scheduled Export fix
Ifgow Your SOC was 88%, your target stop SOC specified was 15%, at a discharge rate of 3.0kW and a battery capacity of 9.5, it would take roughly 138 mins, or at 2:23.
It does look like your battery discharge rate was 1500W if I read the chart correctly?
It might make sense for us to set that to max rate, which the calculation relies on.
I'm sorry but, having read carefully through this thread, I still don't understand why my Scheduled Discharges are stopping earlier nd at higher SOCs than set. My AIO charge and discharge is set to 6kW, as per specifications. I'm away from home with only fridges and freezers running and I want to get through 2 complete charge and discharge cycles per day to get max benefit from Agile and solar but the discharges never complete.
grounded-child
- Edited
JRWM47 Maybe the discharges don't happen at the 6kW rate?
With your 13.5 battery and leaving some margin, for an export between 6:00 and 9:00, you would expect the battery to be empty at shortly past 8:00AM at a discharge rate of 6kW.
Clearly, if there is some DC-AC conversion going on too due to some solar generation, this likely has an impact as well.
With many more schedules now available, you could work around this by setting up a subsequent second export schedule with a SOC trigger condition, and space it 5 mins or so apart from the previous export.
Thanks for the reply.
I've just checked back using the GE app and, yes, over the last few days all my AIO discharges have all been limited to around 3.5kW. The question now is 'why?'.
The GE AIO is rated at 6kW for charge and discharge which is what I have told WW. It can't be due to solar generation as discharges starting at 22:00 when it's dark are also limited to 3.5kW.
I understand your suggested work-around but I'm obviously eager to export my excess stored energy as often and as rapidly as possible.
Any suggestions from WW admin or other users would be most welcome.
JRWM47 It might be worth querying this over on the GivEnergy forums too.
On further investigation, I think it's a G98/G99 issue with my DNO. With GE now shipping AIOs which can discharge at more than the single-phase G98 limit of 3.68kW, I imagine this will be an increasingly common problem. I am applying for G99 and meanwhile will set my discharge period to 4.5 hours. Thanks for pointing me in the right direction.