I can report that last night I used hold from 12am till 6am with a few charging slots in between. The first hold between 48 and 51w dribbled through, 0-3w with the other holds

admin Seems to be better. Last nights results...

Do you need to do the Battery Charge Power changes because you are using timed slots?

    johalareewi

    Do you need to do the Battery Charge Power changes because you are using timed slots?

    Yeah, it's effectively the same as using the Pause button on the Giv app. It's to make sure that during the hold charge periods, there isn't any fluctuation of 100W here and there, which does happen if you're keep AC charge target to current SOC.

      admin it's effectively the same as using the Pause button on the Giv app

      The app pause button pauses charging and discharging but for the WW hold feature, you just want to pause discharging so you could just change the discharge settings and leave the charge settings alone.

      It's interesting that despite the discharge setting being zero, there was still some discharging (a few Watts). Couldn't test the EV bit because the EV charge was during selected slots only. One night it will happen..

      The app pause button pauses charging and discharging but for the WW hold feature, you just want to pause discharging so you could just change the discharge settings and leave the charge settings alone.

      Right, but equally we know we don't want the battery AC charging during hold-charge either, right? So not sure it matters much tbh. Unless I'm missing some elaborate scenario?

        admin Its just that on the screen it says it prevents discharge.

        Although HOLD implies no charge or discharge.

        It is also interesting that the HOLD instruction is sent at the start of the first hold slot but is not released until the end of the charge window (see my inverter log). I would expect the hold to removed at the end of each hold slot block.

          johalareewi

          It is also interesting that the HOLD instruction is sent at the start of the first hold slot but is not released until the end of the charge window (see my inverter log). I would expect the hold to removed at the end of each hold slot block.

          Yeah, made sense to implement like this, and then any charge slots will modify charge power again if it's 0.

          Mat would be helpful if you could charge from the pv if a hold was set during the day?

          Good point.

          Worked fine last night. EV charger didn't get any GE battery during a hold slot.

          But from the logs, it looks like Battery Discharge is set to zero for pretty much all of the charge window rather than just the hold slots.

            johalareewi Yeah, with the idea being that it's being reset at the end. Do you see the reset for charge/discharge power in your Giv log?

              admin Do you see the reset for charge/discharge power in your Giv log?

              Last night breakdown...

              Agile Charge Window is from 00:00 to 06:30
              Selected slots are:-

              First slot at 00:00 all OK.

              First hold at 00:30 both charge and discharge set to zero


              Next charge at 01:30 Charge is restored to 2600 but discharge remains at zero.

              Next hold at 02:30 - Nothing received by inverter

              Next charge at 03:00 no change to charge or discharge values

              Next hold at 04:00 charge set to zero

              Next charge at 05:30 charge resotored to 2600

              Next hold at 06:00 charge set to zero

              Window ends 06:30 - nothing in WW activity log but inverter has this

              Battery charge and discharge both restored.

                johalareewi Thanks for the detailed breakdown, you can see the values that were sent but weren’t changed, by toggling one of the sliders at the bottom of the Giv log.

                All in all, went OK then? Note that the latest release does not reduce charge power in a charge hold slot anymore.

                  admin Simple one last night.

                  GE Inverter log

                  Looks cleaner just using the Battery Discharge Power setting.

                  Just had an interesting situation.
                  Battery was at 96% and there were a few cheap slots coming up just before the peak period.
                  Tumble drier was on so using the GE app, I paused the battery so the tunble dryer would use the cheap electricity and save the battery for the peak slot. This was OK but half an hour later, Wonderwatt issued a PLAY command sequence. There is nothing in the WW activity log (apart from the skipping charge) and the GE app said battery was still paused even though it wasn't.

                  GE log

                    johalareewi So that command was issued as part of the 'disable charge slot', which had just passed.

                    Part of disabling a charge slot (whether a charge happened or not) is to reinstate discharge power (and charge power - gets reset too if it's less than max)

                    Not sure how we could decide not to, and know about other external ways that users might well interact with their Giv systems that we can't possibly all cater for?

                    GE app said battery was still paused even though it wasn't.

                    The GE app is quite prone to still having stale or cached values.

                      admin So that command was issued as part of the 'disable charge slot', which had just passed.

                      Ah. Didn't realide that still happened when a charge slot was skipped due to high SOC value.
                      Still learning how this works.

                        johalareewi It’s all good. I guess we saw it as something that wouldn’t cause any issues at that point. Most logical is to set those values back, as only occasionally you might mean them to be at 0.

                        Hi, relatively new to this and seems a great product. One thing is during the 'gap' periods on agile my battery seems to be half on hold, half not, in that according to the giv portal it's trickling out c.300w with the rest of the load being met by the grid, rather than holding on whatever SOC it's got to in the previous charging window. Could you look into it? I'm tremendous-control. TVM